 Post subject: RF Stat on Combi Boiler, help!
PostPosted: Fri Oct 16, 2009 23:46 
User avatar
Engorged Member

Joined: 18th Aug, 2008
Posts: 370
Help request for plumbing / heating engineers (or would-be engineers)!

I have a Worcester Bosch 240RSF combi and today I bought a Sunvic TLX RFP (an RF room thermostat). Do you think I can wire the fucker in so it works? No. So I need advice.

The boiler has 2 live outs and neutral, it doesn't do volt free. Currently the lives are bridged. The stat receiver has 2 live terminals and a neutral. So how hard can this be? I have removed the bridging and wired it all in. It appears to be behaving correctly, however when the stat temperature drops sufficient to create demand, instead of kicking the boiler in, the receiver just clicks (a relay?) repeatedly and flashes its 2 pointless LEDs.

It seems simple to wire in, I suspect the receiver is faulty, but I bought it through my work's account at a trade supplier, so am expecting them to be shitty when I go back. I just want to be sure it's not me.

Anyone have any experience of this sort of thing?

_________________
Samsung LE40A686
Samsung HT-UP30
Sky+HD
Xbox 360 60Gb
Acer 5920G - Core2Duo T7300. Geforce 8600M. 4Gb RAM
Apple iPhone 3GS
Worcester Bosch 240RSF
Hotpoint WF541 (Graphite)
Beko ZA630 (Graphite)
Centurion CLN-155S
Sharp R209


Top
 Profile  
 
 Post subject: Re: RF Stat on Combi Boiler, help!
PostPosted: Sat Oct 17, 2009 0:08 
User avatar
Paws for thought

Joined: 27th Mar, 2008
Posts: 17160
Location: Just Outside That London, England, Europe
Myfinger wrote:
Anyone have any experience of this sort of thing?


No


Top
 Profile  
 
 Post subject: Re: RF Stat on Combi Boiler, help!
PostPosted: Sat Oct 17, 2009 8:21 
User avatar
Excellent Painter

Joined: 30th Apr, 2008
Posts: 7324
Location: Behind you
Put a jumper on.

_________________
twitter || website
Malibu Stacy. Everybody's favourite back seat driver


Top
 Profile  
 
 Post subject: Re: RF Stat on Combi Boiler, help!
PostPosted: Sat Oct 17, 2009 9:05 
User avatar
baron of techno

Joined: 30th Mar, 2008
Posts: 24136
Location: fife
That should work.
Does the boiler run when it's bridged?


edit: just to explain how those should be wired up:

The boiler has a neutral, a live and an input. When you bridge the input to the live (either with the thermostat relay or a piece of wire), it should start.

The thermostat needs a neutral and live to work, and it also has a switch output (relay contacts) which connects the output to live when it wants heat.

So, just make sure you've got the live connected to the live and the input connected to the output.


The relay shouldn't click "repeatedly" though, it should be on or off.


Top
 Profile  
 
 Post subject: Re: RF Stat on Combi Boiler, help!
PostPosted: Sat Oct 17, 2009 9:25 
User avatar
Chinny chin chin

Joined: 30th Mar, 2008
Posts: 15695
Try flashing the BIOS.


Top
 Profile  
 
 Post subject: Re: RF Stat on Combi Boiler, help!
PostPosted: Sat Oct 17, 2009 9:33 
SupaMod
User avatar
"Praisebot"

Joined: 30th Mar, 2008
Posts: 17081
Location: Parts unknown
Buy an Xbox 360!


Top
 Profile  
 
 Post subject: Re: RF Stat on Combi Boiler, help!
PostPosted: Sat Oct 17, 2009 10:34 
User avatar
baron of techno

Joined: 30th Mar, 2008
Posts: 24136
Location: fife
Hang on, is the receiver like this?

Image

And the boiler like this?

Image


If so, you need to go

Code:
boiler      stat
1           2
2           L AND 3
3           N


Top
 Profile  
 
 Post subject: Re: RF Stat on Combi Boiler, help!
PostPosted: Sat Oct 17, 2009 11:31 
User avatar
Engorged Member

Joined: 18th Aug, 2008
Posts: 370
kalmar wrote:
Hang on, is the receiver like this?

Image

And the boiler like this?

Image


If so, you need to go

Code:
boiler      stat
1           2
2           L AND 3
3           N

Yes. Exactly that. Your diagram for the stat shows a volt free wiring diagram. My stat has that design, but it comes with a wire preinstalled bridging the 2 volt free connections. I read the (useless) instructions as meaning to leave that wire in place for the "standard" installation I am attempting, or remove it in order to wire in the volt free connections for a volt free installation.

Things are also not labelled up as 1, 2 , 3, 4 etc on the stat. Which is shit.

Hold on. I think I may have committed some stupidity by not reading the instructions properly. Cos that's not like me. :)

_________________
Samsung LE40A686
Samsung HT-UP30
Sky+HD
Xbox 360 60Gb
Acer 5920G - Core2Duo T7300. Geforce 8600M. 4Gb RAM
Apple iPhone 3GS
Worcester Bosch 240RSF
Hotpoint WF541 (Graphite)
Beko ZA630 (Graphite)
Centurion CLN-155S
Sharp R209


Top
 Profile  
 
 Post subject: Re: RF Stat on Combi Boiler, help!
PostPosted: Sat Oct 17, 2009 11:41 
User avatar
Engorged Member

Joined: 18th Aug, 2008
Posts: 370
Myfinger wrote:
Hold on. I think I may have committed some stupidity by not reading the instructions properly. Cos that's not like me. :)

Kalmar mate, well fucking done. You made me go and look at what I'd wired in and I saw my OBVIOUS mistake.

I hadn't wired the live into the same terminal as the bridge wire, I'd wired it into SL(off).

Thanks mate! :-

It works exactly as I'd hoped, I can still use the timer / programmer on the combi, but use the stat to control temperature. Ace.

_________________
Samsung LE40A686
Samsung HT-UP30
Sky+HD
Xbox 360 60Gb
Acer 5920G - Core2Duo T7300. Geforce 8600M. 4Gb RAM
Apple iPhone 3GS
Worcester Bosch 240RSF
Hotpoint WF541 (Graphite)
Beko ZA630 (Graphite)
Centurion CLN-155S
Sharp R209


Top
 Profile  
 
 Post subject: Re: RF Stat on Combi Boiler, help!
PostPosted: Sat Oct 17, 2009 12:26 
User avatar
baron of techno

Joined: 30th Mar, 2008
Posts: 24136
Location: fife
Awesome, glad it worked :D


Top
 Profile  
 
 Post subject: Re: RF Stat on Combi Boiler, help!
PostPosted: Sat Oct 17, 2009 13:18 
User avatar
Sitting balls-back folder

Joined: 30th Mar, 2008
Posts: 10140
I want to know why, in late 2009, heating systems aren't properly intelligent yet.

My last two places had programmable blocks of time, so I could specify what temperature I wanted at 4pm on Thursday and so on - but they still only had one thermostat, and each radiator then had a stupid thermostatic valve on.

This place has a simple 24 hour timer, a main thermostat, and the radiators as before.

What I want is to have a thermostat in every room (located optimally, rather than right next to the heat source) which can tell the boiler (so it starts pumping hot water) and tied-in radiators (which open their valves) their temperatures. That should be totally boggo by now.


Top
 Profile  
 
 Post subject: Re: RF Stat on Combi Boiler, help!
PostPosted: Sat Oct 17, 2009 13:22 
SupaMod
User avatar
Commander-in-Cheese

Joined: 30th Mar, 2008
Posts: 49237
My old boiler had a digital timer, so you could set start and stop times differently for each day. But only two start and stop times.
My new boiler has an analogue timer. You can have as many start and stop times as you like, but it doesn't care about days of the week.

FFS.

_________________
GoddessJasmine wrote:
Drunk, pulled Craster's pork, waiting for brdyime story,reading nuts. Xz


Top
 Profile  
 
Display posts from previous:  Sort by  
Reply to topic  [ 12 posts ] 

All times are UTC [ DST ]


Who is online

Users browsing this forum: Majestic-12 [Bot], TheVision and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search within this thread:
You are using the 'Ted' forum. Bill doesn't really exist any more. Bogus!
Want to help out with the hosting / advertising costs? That's very nice of you.
Are you on a mobile phone? Try http://beex.co.uk/m/
RIP, Owen. RIP, MrC. RIP, Dimmers.

Powered by a very Grim... version of phpBB © 2000, 2002, 2005, 2007 phpBB Group.